Severity: Critical
Time Window: 06/18/2024 12:00 AM to 06/30/2024 12:00 AM
The ColoCrossing IDC-1 Buffalo Datacenter, located at 325 Delaware Avenue in Buffalo, is experiencing a temperature rise event. The period of elevated temperatures began during the afternoon of June 18 and was the result of historically high record-breaking temperatures in the region. The extremely high outdoor temperatures resulted in a capacity reduction of the facility's cooling platform as air conditioning heat rejection systems become less efficient during times of exceptionally high ambient temperatures. This condition, joined with two other air conditioners experiencing faults, has resulted in temperatures rising further inside the datacenter space.

ColoCrossing personnel and the facility management team are onsite addressing the situation. External mechanical contractors are scheduled to arrive soon to further aid in the resolution.

Not all areas of the facility are impacted, and the majority of customer devices remain online and uninterrupted. We continue to work diligently to fully solve the temperature rise event and appreciate the patience of those impacted.

Further updates to follow as soon as possible.
发表于 2024-6-19 10:28:07 | 显示全部楼层
G了,99刀杜甫买了半年,一直闲置也从来没出过故障,上个月刚从OVH搬到CCS,这才一个月不到就这么严重的故障
发表于 2024-6-19 10:47:17 | 显示全部楼层
The ColoCrossing IDC-1 Buffalo Datacenter, located at 325 Delaware Avenue in Buffalo, experienced a temperature rise event between the hours of 4 PM ET and 10 PM ET today, June 18. The event has been resolved and temperatures are returning to normal at this time.

The temperature rise event was the result of historically high, record breaking, environmental temperatures in the region. The extremely high outdoor temperatures resulted in a capacity reduction of the facility's cooling platform as air conditioning heat rejection systems become less efficient during times of exceptionally high ambient temperatures. This condition, joined with two other air conditioners experiencing faults, resulted in temperatures rising further inside the datacenter space.

ColoCrossing personnel and the facility management team are onsite monitoring the situation to ensure that all systems continue to operate normally and that the datacenter temperatures continue to return to normal levels.

Not all areas of the facility were impacted by the temperature rise event, and the majority of customer devices remained online and uninterrupted through the duration of the event.

Thank you for your continued business and support.